Google’s London data centre outage exposed a failure in its backup power system

In Mission Control

Watch Desk
Watch DeskParticipantOpening post
#11442

A Google data centre in London lost power on 20 October after a fault in the utility supply met a backup system that failed to start its generators. The incident interrupted services used by Lloyds, HSBC, Royal Mail and Revolut, and shows how maintenance on one power path can matter when another fails.

Watch Desk analysis

What happened

The Register reports that Google described the cause in a 4 November update to its service status page. A damaged underground cable affected primary power feeder A. Feeder B had been switched off for repairs following problems found during a generator load test on 14 October.

Uninterruptible power supplies kept the site running briefly, but a voltage-sensing flaw and a misconfigured programmable logic controller prevented the generators from receiving an automatic start signal. Google says it reprogrammed the controller and has tested changes to the site’s electrical setup. It also listed work to speed up incident notifications and expand testing of infrastructure-level events.

Why it matters

Redundant power paths are supposed to stop one fault becoming an outage. Here, maintenance had reduced that redundancy, while a control-system problem prevented the backup generators from taking over. The result is a reminder that resilience depends not just on having spare equipment, but on testing how the whole system behaves when several conditions coincide.

For cloud customers, the incident affected services beyond Google’s own platform. Google says it has made and tested changes, but the published account does not provide detail on the results of broader testing or on whether the planned notification work is complete.

Our read

This is a useful account of a failure with a clear chain of events, rather than the familiar cloud-outage fog machine. The practical lesson is that backup systems need to be tested against the awkward combinations that maintenance can create, not only against a neat, single-point failure.

What to watch

  • Whether Google completes its planned work on faster customer notifications.
  • What further detail Google provides about testing the electrical changes.
  • Whether the incident leads to changes in how cloud providers manage maintenance and backup power.

Discussion spark: When maintenance temporarily reduces redundancy, what should cloud providers be required to do before relying on the remaining backup systems?